Need Assistance with TACO RMB
Steve_210
Member Posts: 647
Hi,
I was going to use the TACO RMB as a setpoint control but outdoor design needs to be turned off. I couldn't find a way to do this from the directions. Could someone please help me with this?
Thank you
I was going to use the TACO RMB as a setpoint control but outdoor design needs to be turned off. I couldn't find a way to do this from the directions. Could someone please help me with this?
Thank you
0
Comments
-
Disconnect outdoor sensor?
I seem to recall that would do it...0 -
Setpoint operation of the RMB
When in the adjust menu, you need to program the OUT DSGN (outdoor design) to OFF.
Also program the Delta T to OFF
Then program your MIX TARG (mix target temp) to your desired temp. The Range is 60-200 and the default is 140.
Enjoy
Dave HDave Holdorf
Technical Training Manager - East
Taco Comfort Solutions
0 -