Munchkin 140 has code PrO
Topper1
Member Posts: 2
How do I reset boiler so it has enough pressure to come back on? Or is this the problem? Could there be something else. unit is 8 years old.
0
Comments
-
Munchkin boiler
Hold on: Gas pressure or hydronic water flow pressure? Which error code specifically do you see?
Munchkins are okay with efficiency and general design, however their controls have a somewhat poor name in the Hydronic review community.
Cheers0 -
water pressure
PRO - is "low water pressure" - The water pressure switch is there to protect the boiler from low water/pressure conditions. Check to see what water pressure you have on the system. If it is below 12 # you need to find out what the problem is and correct it.
If your system is below 12#, the water pressure switch is just doing its job by alerting you to an issue.
If there is an issue with water pressure, could be failed expansion tank, failed pressure-reducing valve, etc.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements