Modine infrared heater
Techman
Member Posts: 2,144
in Gas Heating
,overhead in a shop .The ignition control is missing,the units spec sheet says that a 15sec pre-purge,35 sec trial for ign ,and at the moment I'm assumeing a one time lockout.Mfrg says no parts available ,out of stock. How would I track down a replacement Ignition Control.Does this mean anything---mark-10x-117-15-35-35-e-0-1-2
0
Comments
-
IR heater
Did I read that correctly, 35 sec trial? Pre-purge should be 90 sec plus. Trial for ignition sounds a little excessive, but anything is possible. Fenwal still makes ignition modules for this purpose and although they shed the gray box in appearance, the work flawlessly. What is the unit using for flame sense? Mercury?
Peace
Mike T.0 -
Infrared
Those #'s are in the service manual. Flame sensor/spark tip are both on a 3/4 " x 3" plate that screws onto the unit just downstream of the burner0