Metering heat
radmix
Member Posts: 194
Would anyone have a suggestion on a brand of meter that can be used to separate the heating bills on a building that has a boiler with 8 zones of heat. I remember looking into this some time ago and from what i can recall you would need a device that meters flow and temp to get a BTU output for each zone.
0
Comments
-
Why go through all that?
The same btus are available to all zones, so time would reflect load, and personal preference.Am I not thinking right?0 -
metering
These are some what reasonable
http://www.kele.com/Catalog/07%20Flow/PDFs/380%20Series%20Catalog%20Page.pdf
Most are very pricy and can be troublesome over time.
good luckThere was an error rendering this rich post.
0 -
metering
Time doesn't reflect load with weather response controls. Also Two separate temps in system, Panel radiators and slab radiant0 -
Temp and flow can measure output
This can be done but costlyThere was an error rendering this rich post.
0 -
I
guess btus per hour wouldn't apply in this case then.0 -
Metering
Are all the apartments each on a single zone?
Maybe a run-time meter could be put on each zone pump. While the pump runs, the meter advances. From the combined total of meter readings, each tennants share can be computed.--NBC0 -
Seemed Fair To Me
Regardless of the controls or emitters, the run time of each zone tells the story.0 -
Meters
If the high Temp panel radiators run for 1 hr. and the low temp radiant runs for 1 hr. are you transferring the same amount of Buts? Plus if a zone is running when its 30* out and another zone runs when its 60* out, Both run at the same length of time I don't think it would be accurate to assume your transferring the same amount of Buts0 -
Assumptions
The assumption would be, that the zone would run long enough to transfer enough btus to compensate for the heat loss of the area. The high temp emitters would run shorter and more frequently. The radiant would run longer initially, and less frequently.If a zone with high temp emitters chooses to keep the zone at 90*, the time will reflect it, and so will their portion of the bill.You make the necessary btus available.They use them how they prefer, and pay accordingly.0 -
Assumptions
duplicate0 -
Heat meter
I see the Grundphos magna has a built in heat meter, and wireless as well.--NBC0 -
metering
Were zoning using zone valves with one ECM Circ.0 -
heat metering
i think the runtime meters will still work, as the zone valves are energized to stay open, right?--nbc0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements