Boiler Sizing

Sil
Member Posts: 71
Forgive me but I have another boiler sizing question.
I have a 15 year old Dunkirk boiler (model # 4ES1.85C) which is 259MBH input, 215 MBH Heating Capacity and 671 sq ft of radiation.
I have a small leak in the above ground oil tank and am doing a gas conversion. I was initially considering simply installing a Carlin EZ - Gas, but the install prices are so high I am thinking about changing the whole boiler (esp. considering the utility will give an $1000 rebate for the boiler swapout).
So I the plumber I was thinking of using is recommending a Burnham IN6 (175MBI input, 144 Heating Capacity and 450 sq ft of steam. At first I think this boiler must be too small (based on the boiler I currently have). So I tried computing the sizing myself...
In my whole house I have 3 radiator types.:
-8-3/4" tube type is most prevalent (68 sections in total split across 7 radiators)
-5" tube type in baths (10 section split across 2 radiators)
-20" tall sunrad convectors (28 sections split across 2 convectors)
If my calculations are right, the big rads are 238sqft of steam, small rads are 23sqft and the convectors are 63sqft. So I have a total of 324sqft.
So while I originally thought the IN6 was undersized (based on what I have in the basement now), I am wondering if its may actually be oversized. Thoughts?
I have a 15 year old Dunkirk boiler (model # 4ES1.85C) which is 259MBH input, 215 MBH Heating Capacity and 671 sq ft of radiation.
I have a small leak in the above ground oil tank and am doing a gas conversion. I was initially considering simply installing a Carlin EZ - Gas, but the install prices are so high I am thinking about changing the whole boiler (esp. considering the utility will give an $1000 rebate for the boiler swapout).
So I the plumber I was thinking of using is recommending a Burnham IN6 (175MBI input, 144 Heating Capacity and 450 sq ft of steam. At first I think this boiler must be too small (based on the boiler I currently have). So I tried computing the sizing myself...
In my whole house I have 3 radiator types.:
-8-3/4" tube type is most prevalent (68 sections in total split across 7 radiators)
-5" tube type in baths (10 section split across 2 radiators)
-20" tall sunrad convectors (28 sections split across 2 convectors)
If my calculations are right, the big rads are 238sqft of steam, small rads are 23sqft and the convectors are 63sqft. So I have a total of 324sqft.
So while I originally thought the IN6 was undersized (based on what I have in the basement now), I am wondering if its may actually be oversized. Thoughts?
0
Comments
-
Sizing
If you calculations are correct and your mains are insulated and very well vented I would go for IN5 at 358 sq ft, would not cycle and satisfied thermostat in one long cycle at low pressure0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements