Follow up to "possible blocked radiator" situation
Options
hws
Member Posts: 43
Some of you might remember my thread regarding a "possible blocked radiator" which seems to actually be a direct-return system with a balancing problem>
Well today I began the process of trying to remedy the problem. First thing I tried was, thinking that maybe I made a boo-boo during the roughing in stage, cross the supply and return lines at point A in the attached diagram. Re-filled the system, purged air, and started it up again, and within minutes the whole zone, including the problem radiator, was heating. With the supply and return to the sub-zone crossed, every rad in the zone received heat. So far, so good.
I then took readings with the infared laser thermometer to see how out-of balance everything was. The two top left rads were the hottest at 130 degrees, the problem one was around 105.
I think with valves installed to throttle flow to the two top left rads, I can send some more heat to the sub-zone and hopefully even things out.
Well today I began the process of trying to remedy the problem. First thing I tried was, thinking that maybe I made a boo-boo during the roughing in stage, cross the supply and return lines at point A in the attached diagram. Re-filled the system, purged air, and started it up again, and within minutes the whole zone, including the problem radiator, was heating. With the supply and return to the sub-zone crossed, every rad in the zone received heat. So far, so good.
I then took readings with the infared laser thermometer to see how out-of balance everything was. The two top left rads were the hottest at 130 degrees, the problem one was around 105.
I think with valves installed to throttle flow to the two top left rads, I can send some more heat to the sub-zone and hopefully even things out.
0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements