Hot water zone question
Tim_64
Member Posts: 76
I need to add a hot water zone to my Weil-Mclain SGO-4 boiler to provide heat to the kitchen in my old house... Its a Honeydew
With the help from a friend who is a NYC savvy HVAC (STEAM) contractor I did the initial install with his help..
He is now contracted with FEMA for the foreseeable to restore heat and hot water to those in great need.... My house and property were spared
And not wanting to bother my friend with questions while he is buried with work....
I ask the collective (some preamble LOL)
I was planning to take the water for the hot water zone from the supplied tapping "U1" and return the water and plumb the by-pass from the boiler drain...
Looking more closely I'm not sure this can be done with future maintenance in mind.... All the fittings would prevent the boiler door from swing completely open.
So after all the long winded intro
Can I?
Have the supply, by-pass, and return plumbed from three separate tappings
Supply = U1
Return= "H" or boiler drain
By-pass feed = "B1"
TIA
With the help from a friend who is a NYC savvy HVAC (STEAM) contractor I did the initial install with his help..
He is now contracted with FEMA for the foreseeable to restore heat and hot water to those in great need.... My house and property were spared
And not wanting to bother my friend with questions while he is buried with work....
I ask the collective (some preamble LOL)
I was planning to take the water for the hot water zone from the supplied tapping "U1" and return the water and plumb the by-pass from the boiler drain...
Looking more closely I'm not sure this can be done with future maintenance in mind.... All the fittings would prevent the boiler door from swing completely open.
So after all the long winded intro
Can I?
Have the supply, by-pass, and return plumbed from three separate tappings
Supply = U1
Return= "H" or boiler drain
By-pass feed = "B1"
TIA
0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements