circulator sizing
STEAM DOCTOR
Member Posts: 2,236
I have a customer with home 3 stories high(aprox 30 ft high). Home is 34' x 19'. The entire home is served by one forced hot water loop. The supply and return are 1 1/4". There is aprox 125 mbtu going through the loop. What would be an appropriate circulator for this situation? Thank you
0
Comments
-
rad takeoffs
I cant see what is doing with take offs but I am assuming that this is a monoflow system. House is aprox 50 years old.0 -
head
How do you figure head when the main is 1 1/4 and the radiator takeoffs are 3/4" or 1". This is a divertor T system.0 -
circulator
simple sizing is : head=(30+34+19)x2*0.06=9.96 feed of head
on 20F delta t one gallon per minute delivers 10,000 btuhr, 125000/10000= 12.5 gpm
if you take chart on the pump, lets say like this one http://www.taco-hvac.com/uploads/FileLibrary/101-084.pdf and find point corresponding to those numbers, the closest curve to the right will be your pump
you can check this one out http://s3.pexsupply.com/manuals/1350570919940/83616_PROD_FILE.pdfGennady Tsakh
Absolute Mechanical Co. Inc.0 -
Basic Formula Head
Longest run from the outlet of the circulation through the system back to the inlet
Side if the circulator x 1.5 x .04 = head
100' x 1.5 x .04 = 6' headThere was an error rendering this rich post.
0 -
Circulators:
Box of stale donuts says that a 007 would work fine. Or a Wilo Star 21 three speed on #2.0 -
my box of donuts
my box of donuts after looking at the chart said taco 0014.
007 1t 12.5 gpm will max only 6.5 feet head. unless radiators over sized, and delta T 40F 008 might work.
Just my opinionGennady Tsakh
Absolute Mechanical Co. Inc.0 -
head
Chris , 30+34+19 is max run =85 supply and 85 return, total run 170 feetGennady Tsakh
Absolute Mechanical Co. Inc.0 -
Based On
the limited amount of info the original poster is giving i would agree on the run length.
170 x 1.5 x.04 = 10.2' head
Needs a pump that will do 12.5gpm @11' head. I like to round up.. Grundy 26-99 3-speed would be my choice.There was an error rendering this rich post.
0 -
load
125,000 BTU/hr actually going through the loop, or going into the gas valve at max firing rate? Was a heat loss calc done?0 -
26-99F
I like the Grundfos pumps the best.
BUT - If you are going to use a wet rotor pump make D** sure to put a 100 mesh strainer in front of it on that old system.0 -
DIRTMAG
for wet rotor pumps we started to offer this http://www.caleffi.us/en_US/Technical_brochures/01137/01137.pdf instead of the regular strainer.Gennady Tsakh
Absolute Mechanical Co. Inc.0 -
Dirtmag
That will seperate dirt but stuf can get through it on and if it gets into the wetrotor pump it won't do the pump any good.0 -
magnet
It has a magnet attached to it, and magnet stops all the magnetic rust particles. Periodically magnet is removed and dirtmag is flushed trough bottom valve. It prevents magnetic rust going to wet rotor and sticking there. Dirtmag is designed with specific purpose to protect wet rotor circulators working in magnetic metal systemsGennady Tsakh
Absolute Mechanical Co. Inc.0 -
Wet rotor pumps
I have seen a lot of non magnetic stuff in the impellar of the wet rotor pumps. Throws them off balance and that imbalance tends to destroy the impellar.0 -
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements