Thermal expansion

jjheat
jjheat Member Posts: 35
I have had several customers that were without power for 10 days. Power came back on and their cast iron hot water boilers started up and soon after starting, blew the relief valve and made a mess. I attribute this to cold 40 degree water coming back from several large heating zones. Am I correct??

Comments

  • JStar
    JStar Member Posts: 2,752
    Relief

    I wouldn't think the cold return would cause this to happen. What kind of expansion tanks are on the system? Do they still have air in them? Was the water main worked on, possibly causing a spike in water pressure?
  • jjheat
    jjheat Member Posts: 35
    Thermal expansion

    But if the whole system and boiler were stone cold wouldnt the feeder have fed some water to maintain pressure loss of the stone cold water??

    1 of the systems has extrol 90 that I installed last year on the spirovent before any pumps(pumping away).Water main was not affected at all and has new feeder as well.
  • JStar
    JStar Member Posts: 2,752
    Pressure

    If you do some very crude calculations, the pressure could have gone to about 10 psi at 40F. So, it's possible. I didn't think that would be a big enough pressure change to make a difference.
This discussion has been closed.