Comparing hot water systems and boilers

MLA
MLA Member Posts: 5
Recently bought a house in coastal New Hampshire and need to replace the very ancient boiler (hot water baseboard heat.) Got one quote for a Peerless WBV3 boiler with Beckett Burner and Domestic Coil. Got another for Biasi Model B10-4 with Riello burner and Heat-Floss indirect hot water heater HF-40. We don't know much of anything about any of this and are looking for guidance re: the advantages/disadvantages of the domestic coil v indirect and also about the two different boilers. Any help will be much appreciated, the less technical the better!

Comments

  • SWEI
    SWEI Member Posts: 7,356
    comparing hot water systems

    The indirect will save on fuel during the summer.  If it's sized properly, you may be able to use a smaller boiler depending on the system size.  Did either or both of your proposals include a measurement of your existing baseboard, or did they just look at the nameplate on the existing boiler?
  • MLA
    MLA Member Posts: 5
    comparing hot water systems

    Both vendors are familiar with the house and the heating system there. 
  • SWEI
    SWEI Member Posts: 7,356
    vendors

    Did either or both do a heat loss calculation on the house?
  • MLA
    MLA Member Posts: 5
    vendors

    I don't even know what that means but I guess that's a question I should ask them.
  • SWEI
    SWEI Member Posts: 7,356
    heat loss calc

    Needs to be done for each room, plus a total.



    The total is used to determine the correct size for the boiler.  This plus the domestic hot water demand (another calculation the contractor or engineer will need to do) will determine the size of the indirect.



    The room-by-room numbers are used together with with the length of baseboard in that area plus a derating chart for your brand of baseboard to determine the system supply temperature needed at design conditions.  If the room-by room balance of radiation to heat loss is out of whack, you should be informed and given options.  If the boiler can be configured to deliver a variable output temperature based on an outdoor reset scheme, you will get better indoor comfort and burn less oil.