Sizing an inverter for a simple one-pipe steam system
Jim Murphy
Member Posts: 15
Hello Steamheads,
Posted here because I thought the response would apply to to more than just steam systems. Getting very cold here in Jersey - day 8 with no power and at least 3 more days expected.
I'd like to hook up an inverter to the boiler and get her running before the wife bugs out on me.
The boiler is a Utica PEG-C steamer, 24Volt Electronic Ignition and Low-Water cutoff. Simple one-pipe gravity return steam system. Electronic Damper is inoperative even with power, but is open.
Can't find how much amperage the unit draws so that I can figure out wattage to size the inverter.
Can anyone help me? For any who have done this, any other considerations on the battery side that I should think about.
Thanks in advance for any and all help,
Jim
Posted here because I thought the response would apply to to more than just steam systems. Getting very cold here in Jersey - day 8 with no power and at least 3 more days expected.
I'd like to hook up an inverter to the boiler and get her running before the wife bugs out on me.
The boiler is a Utica PEG-C steamer, 24Volt Electronic Ignition and Low-Water cutoff. Simple one-pipe gravity return steam system. Electronic Damper is inoperative even with power, but is open.
Can't find how much amperage the unit draws so that I can figure out wattage to size the inverter.
Can anyone help me? For any who have done this, any other considerations on the battery side that I should think about.
Thanks in advance for any and all help,
Jim
0
Comments
-
borrow a 1kW or larger inverter
From a friend - should be more than enough output capacity but you still need to test: Does everything work OK on the inverter waveform?
Assuming everything runs OK, measure the draw using a clamp-on ammeter at startup, while steaming, and after shutdown while idling.0 -
Thanks
Ended up getting through to Utica. Couldn't give me exact current draw, but indicated that with such a simple package, it couldn't draw over 2 amps at 24.5Volts, so 49 Watts. Bought a cheap 100W cigarette lighter inverter, wired her in in 15 minutes, in the dark with a flashlight, and she fired. Warm a few hours later - we joyously watched the thermostat rise!
Such a small inverter can only handle a small load, but with the Nor'easter bearing down, we needed heat!
My only concern was drawing down the battery, so I left the car at idle, didn't care about the gas. Fortunately it didn't use much.
Of course the power came on at 1am... Wish I had done the inverter days ago.
This was so easy that I'm surprised that this it is not more common knowledge.0 -
sounds close to my system
simple 1 pipe steam with damper, LWCO, flame roll out switch, gas fired.. The only thing different I have is a taco circulator pump for the hot water baseboard tapped off the boiler...
Luckily I had power restored in 2 days so it never became an issue, but to sit in a cold house and freeze when all you needed was a cheap inverter, what a kick in the butt!
Best of luck to you0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements