how often to blow down boiler
Tom S.
Member Posts: 94
I think that is the right term....
An uncle has a house with a relatively new steam boiler, let's say 5 yrs old. It has an auto water fill. Unfortunately he has suffered a stroke and will be out of his house for months and it will be empty. We are turning the heat down to 55 or so, but obviously the boiler will be firing throughout the next months.
My question is how often should I ask someone (neighbor/house looker-after person) to blow down the boiler? Weekly? Biweekly? Less often? I'm talking about taking out a gallon or two of sludgy water and letting the autofill replace it.
Thanks,
Tom
(btw I do have a freeze/water-on-the-floor/loss-of-power alarm in place which will call me if any of those things go wrong).
An uncle has a house with a relatively new steam boiler, let's say 5 yrs old. It has an auto water fill. Unfortunately he has suffered a stroke and will be out of his house for months and it will be empty. We are turning the heat down to 55 or so, but obviously the boiler will be firing throughout the next months.
My question is how often should I ask someone (neighbor/house looker-after person) to blow down the boiler? Weekly? Biweekly? Less often? I'm talking about taking out a gallon or two of sludgy water and letting the autofill replace it.
Thanks,
Tom
(btw I do have a freeze/water-on-the-floor/loss-of-power alarm in place which will call me if any of those things go wrong).
0
Comments
-
Blowing down the boiler
It is the float-type LWCO which is most important to be blown down (or flushed)., at least once a month. However, it would be better to valve off the auto-fill, and have the neighbor check the boiler every few days at first, and then weekly. You do not want a leak in the system to go on just being compensated by the auto-fill, and if it is valved off, then any loss of water can be seen and dealt with.--NBC0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements