Burnham MPO 84 andn indirect piping question

Jake2010
Member Posts: 24
I have decided to install a Burnham MPO 84 along with my existing Weil Mclean 40 gal indirect. The DHW will run on priority, I also have 2 heating zones. Will I be OK with 1 inch supply and and Taco 007 pump for indirect? My concern is that the smaller boiler will not be able to keep up with the flow to the indirect. Would a 1 inch zone valve be an acceptable alternative to the seperate DHW pump? What is the advantage of using pump over zone valve for indirect?
0
Comments
-
1 inch is fine
On priority the boiler should have no problem keeping up with the indirect . Even without priority . Unless you have a huuuuge hot water demand .....
We've installed a few boiler / indirect combos with zone valves and they are trouble free .
Just remember the boiler water return from the indirect has to go into the lower tapping in the back of the boiler . Where the boiler drain goes . Not where the system return connects in the boiler . Good luck with the install !0 -
You can
Also pipe it primary/secondary and leave the boiler drain alone.There was an error rendering this rich post.
0 -
recommended burner for Burnham MPO 84
Thanks for the responses that I received. Any recommedations for oil burner for the MPO 84, Beckett AFG vs Carlin EZ 10 -
Burnham
Only shows a Beckett/Riello for the 84. If your going for the carlin,I would check with Carlin firstThere was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 159 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 941 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements