Sunrad EDR
eclark
Member Posts: 33
Bought a house last year that has mostly Sunrad (or sunrad style) radiators. I'm just trying to see how many EDR for the units, but can't find any guidance. Anybody know where I can get it?
Thanks,
Eric
Thanks,
Eric
0
Comments
-
Try This
Go to the section "Sizing radiation for steam boilers" http://www.comfort-calc.net/Steam%20Information.html0 -
There are
There are 2 sizes to choose from in this pdf from the library here.
M 5X20 is 2.25 EDR per section,
M 7.25X23 is 3.40 EDR per section
http://www.heatinghelp.com/files/articles/928/299.pdf0 -
-
The American Standard Catalog
gives those ratings as 2.0 ft.² and 3.0 ft.² EDR, respectively. I wonder why there's a discrepancy?Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
Thanks guys
Reason I ask is because when we moved in, there were two places where radiators had been disconnected and removed. I have no idea why. If I find out that I've got only 275 SF of EDR installed but that my boiler has capacity for 360, I can reinstall those radiators without compromising the system, right?0 -
Heat Loss
Not only will it not adversely affect the system, if you do a heat loss of the areas they've been removed, you will probably discover they're needed.0
This discussion has been closed.
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 51 Biomass
- 419 Carbon Monoxide Awareness
- 91 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 922 Plumbing
- 6.1K Radiant Heating
- 375 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 16 Recall Announcements