Loss of pressure across pilot solenoid

JEMM55
Member Posts: 47
in Gas Heating
I have a Weil McClain model 580 with a midco burner. I am having a problem with the pilot it lights only intermittently when the boiler calls for heat or hot water.
Everything is freshly tuned...ignition, flame rod, all electronics ignition check out and there is excellent spark.m the main gas pressure from the main is over 6in col water. The pressure before the solenoid is also 6 after a 30 inch run past the regulator. The burner calls for 3.5 in column after the solenoid. No matter what I do I cannot figure why the pressure drops to 1.8 max. New solenoid, everything clean but can't get higher pressure so the pilot is lighting intermittently. Any ideas are welcome........help?
Alan
Everything is freshly tuned...ignition, flame rod, all electronics ignition check out and there is excellent spark.m the main gas pressure from the main is over 6in col water. The pressure before the solenoid is also 6 after a 30 inch run past the regulator. The burner calls for 3.5 in column after the solenoid. No matter what I do I cannot figure why the pressure drops to 1.8 max. New solenoid, everything clean but can't get higher pressure so the pilot is lighting intermittently. Any ideas are welcome........help?
Alan
0
Comments
-
Gas
What is the main pressure when the pilot solenoid opens? Does it stay at 6+ inWc? Do you have proper voltage going to the solenoid?0 -
main pressure unchanged and separate 110 feed for solenoid
?0 -
main pressure unchanged and separate 110 feed for solenoid
?0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements