Oil To Gas Boiler Conversion

Heat
Heat Member Posts: 2
I am in the process of converting the existing oil boiler which is U.S radiator Corp red Top size A6, model # 64479. I am considering  the Columbia MCB series gas boiler. would you recommend I go with 75,000 BTU or 100,000 BTU input. My town homes heating area has 7 radiators & is approx. 1,000 sq ft.



Chris,

Comments

  • RDSTEAM
    RDSTEAM Member Posts: 134
    Heat loss needs to be done

    Rad size and home soze doesnt dictate boiler size. Complete a heat loss calc and you will get you answer. Slant fin has a prettygood program.
  • Paul48
    Paul48 Member Posts: 4,469
    edited October 2012
    You

    Have to calculate the heat loss of the structure. Then match the boiler according to that.If no one posts the link to the download of the calculator, I'll post it later, when I get home.