Tekmar 508 and Taco Zone Controls
fatty_2
Member Posts: 54
Hi there,
I am running into issues with this set up. The story: I built this system many years ago, maybe 5... and it sat for some years in a house that was never finished. Thieves eventually broke in and cut out all of my copper work... leaving the electronic components and some pumps just dangling in the wind.
A friend of mine bought the house - and completed it - and as a favor I offered to rebuild the system. Unfortunately I do not remember what my design was... I just did my best to reimagine what I had originally planned and tried to fill in the blanks.
The issue I am hitting right away in with the Tekmar thermostats. When I connect them to the Zone control (with 120v circulators, not zone valves) They light up, but show no display. No numbers, no info, no error messages or codes. They also immediately cycle on the zones... each circulator slams on at once.
One relay clicks rapidly and the circulator fails to start. I am guessing that one is frozen from sitting out of use for so long (the system was drained but wet enough to rust I suppose). In this picture I have them disconnected to stop them from running constantly.
The thermostats I really have no guesses for... but this was my first time using this set up. I am not even gotten to the point of wiring the boiler, aquastat, etc. but just wanted to see that the thermostat wiring I had originally placed had not been damaged during the remodel.
These Tekmar units have a slab sensor as well... which is 2 wire. They control 2 isolated radiant slabs within the home.
Thank you so much... for your time
Tom
I am running into issues with this set up. The story: I built this system many years ago, maybe 5... and it sat for some years in a house that was never finished. Thieves eventually broke in and cut out all of my copper work... leaving the electronic components and some pumps just dangling in the wind.
A friend of mine bought the house - and completed it - and as a favor I offered to rebuild the system. Unfortunately I do not remember what my design was... I just did my best to reimagine what I had originally planned and tried to fill in the blanks.
The issue I am hitting right away in with the Tekmar thermostats. When I connect them to the Zone control (with 120v circulators, not zone valves) They light up, but show no display. No numbers, no info, no error messages or codes. They also immediately cycle on the zones... each circulator slams on at once.
One relay clicks rapidly and the circulator fails to start. I am guessing that one is frozen from sitting out of use for so long (the system was drained but wet enough to rust I suppose). In this picture I have them disconnected to stop them from running constantly.
The thermostats I really have no guesses for... but this was my first time using this set up. I am not even gotten to the point of wiring the boiler, aquastat, etc. but just wanted to see that the thermostat wiring I had originally placed had not been damaged during the remodel.
These Tekmar units have a slab sensor as well... which is 2 wire. They control 2 isolated radiant slabs within the home.
Thank you so much... for your time
Tom
0
Comments
-
Hi fatty.
Considering that the house was ran sacked, think like everything is damaged. What I am thinking is a short somewhere in the lo vac control circuitry. Have you tried to jump out your t-stats manually with jumper? At least we can verify if the Taco controller is good or bad. Since you mentioned chattering relay, I does sound like a short. From there check wiring at wall one at a time. I am thinking since you can start from the Taco controller first, then jump the heat circuit out at the t-stat locations. This will take some time, but you need to find the faulty circuit before you can go any further. I'll bet the intruders possibly ripped through a wire or two.
Mike T.0 -
Tekmar 508 wiring
This thermostat is a 4-wire stat. 2 are for power and two for endswitch.
Wiring to the ZVC board, the endswitch wire go to "TT" on the ZVC.
Your 24 volt power to the stat can also come from the ZVC, but use the terminal on the top left on the controller.
Dave HDave Holdorf
Technical Training Manager - East
Taco Comfort Solutions
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements