What makes a boiler sound like a Moose?
KCA_2
Member Posts: 308
And it does... Starts off slow but..... I've got two boilers that are moaning like this..
Drives the owner crazy... Me too!
Ideas?
:-) Kca
Drives the owner crazy... Me too!
Ideas?
:-) Kca
:-) Ken
0
Comments
-
Sound
Leak?
What kind of boiler?0 -
moose noise??
Well I went and checked with my know it all son-in-law and he says it's only during mating season.
Now look, I don't what you guys are doing out there, but leave the damn moose alone!0 -
sounds like....
it is out of tune. Was it set up w/ a combustion tool? How old is the install? When was it cleaned last? Make and model of the unit?0 -
Make & Model
It's a Weil McLain CGI 7 P IN
Just cleaned
Draft -.1
CO 14PPM
CO2 5.5
O2 11.2
The moan isn't in the gas train... I had to extend the vent & make a snorkle of sorts outside because the existing vent was about 12" from the ground here in Colorado...
Owner e-mailed me and said that when it comes on for 5 minutes the thing sounds like a moose.. Lol...
Kca:-) Ken0 -
Does it have....
Glycol / anti freeze in it?0 -
under fired
I guess it's on natural gas and those numbers indicate, under fired. The CO2 reading should be 8-9% and the O2 closer to 6% while keeping CO under 100 ppm and if it's LP, you're even more under fired. Increase the manifold pressure to get in that range. If you get much over 4.0 w.c. and still not in range, check your gas orifice size, they may not be high altitude. I'd be concerned about snorkeling up with exposed vent and possible freezing, it's certainly not pictured that way in the venting instructions.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements