wet steam from vents of a single pipe system

sandcreek
sandcreek Member Posts: 8
I have a one pipe steam system, boiler installed in 1997, and we have been in the home for about a year.  I have wet steam coming out of most of my vents and have had it last seaon too.  nI know this is wrong as only air should be pushed out.

I have read as much as possible to figure out how to stop it and now I am really confused.

Can anyone suggest what are a few of the most simple steps a homeowner should try 1st to take care of this before I call for a Pro to make a service call?

Comments

  • Paul48
    Paul48 Member Posts: 4,469
    Vents

    Make sure there are main vents and plenty of them, in the right locations.Run the pressure on the boilers, at the absolute minimum( main vents allow that).Make sure the radiator valves are fully open, or fully closed, not in between.Make sure the radiators are pitched ever so slightly towards the valve end. Purchase the book "We Got Steam Heat" from this site. One of the best investments you'll make.