Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Guard Dog Wiring...

kcopp
Member Posts: 4,517
I am wire up one of these for the 1st time... Buderus G124xII w/ the RB-24E w/ the Honeywell 8148E aquastat.
The diagram they give is pretty good except for 2 things I am not sure on....
>Do I remove the jumper between W and Z?
> Not sure where to wire in the 2nd yellow wire going to TR?
<a href="http://s3.pexsupply.com/manuals/1320960093621/67941_PROD_FILE.pdf">http://s3.pexsupply.com/manuals/1320960093621/67941_PROD_FILE.pdf</a>
page 4 at the bottom
ty,kcopp
The diagram they give is pretty good except for 2 things I am not sure on....
>Do I remove the jumper between W and Z?
> Not sure where to wire in the 2nd yellow wire going to TR?
<a href="http://s3.pexsupply.com/manuals/1320960093621/67941_PROD_FILE.pdf">http://s3.pexsupply.com/manuals/1320960093621/67941_PROD_FILE.pdf</a>
page 4 at the bottom
ty,kcopp
0
Comments
-
Wiring
Keep the jumper.
The yellow wires interrupt the burner control in series. Treat it like a limit/safety.0 -
that helps....
a little bit but I need to know exactly were I put that wire.0 -
One
to TR, one to B1, like the drawing. Blow the drawing up, to make it clearer.0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements