I usually test gas pipe with my air compressor set to 5# and leave it off to the gas controls or disconnected and capped.
This came up. I piped up some gas that I want to test because there are a lot of leak sources. It's LP. I asked someone who installs and services a lot of LP only. He said to just turn on the gas. That way I won't overpressure anything. There is a 2" Maxitrol in the gas train.
I thought of using my air compressor set to some low pressure (5# or less, and feeding it through a 1/2" Maxitrol regulator, which I could set to 14" or such, use my manometer and soap, and not be worrying about loose gas if I have to fix a leak.
What do others do in this situation? I have test ports all over so I can get clever with the air. I'd rather not test with the gas. And break anything.
This came up. I piped up some gas that I want to test because there are a lot of leak sources. It's LP. I asked someone who installs and services a lot of LP only. He said to just turn on the gas. That way I won't overpressure anything. There is a 2" Maxitrol in the gas train.
I thought of using my air compressor set to some low pressure (5# or less, and feeding it through a 1/2" Maxitrol regulator, which I could set to 14" or such, use my manometer and soap, and not be worrying about loose gas if I have to fix a leak.
What do others do in this situation? I have test ports all over so I can get clever with the air. I'd rather not test with the gas. And break anything.
0
This discussion has been closed.
Categories
- All Categories
- 86.9K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 109 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 105 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 971 Plumbing
- 6.3K Radiant Heating
- 386 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements