Uhhh....Which Vaporstat?
Steam_Starter
Member Posts: 109
Dialing in my single pipe system for the season....got pressuretrol set to 2 psi out, .5 psi in. However, I want to sensitize the system even further. Dialed in main venting to about 5.5 CFM on a 45 x 2" run (most I can fit in this joist bay on an antler) and want to keep the pressure low and accurate.
Any suggestions on a good Vaporstat for a Utica Starfire 3 boiler?
Thanks in advance...
Any suggestions on a good Vaporstat for a Utica Starfire 3 boiler?
Thanks in advance...
"Hey, it looks good on you though..."
0
Comments
-
The one you want
is the Honeywell L408J1025. Its range is 0-16 ounces.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Thanks Steamhead!
Coming thru for the board, as usual!
Have a good one..."Hey, it looks good on you though..."0 -
What's the difference
between:
Honeywell L408J1009 and
Honeywell L408J1025 ??8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
The Honeywell L408J1025 ...
Makes the circuit on pressure rise only. The Honeywell L408J1009 will make or break the circuit depending on how it is wired. For Boiler control, you want to break the circuit on pressure rise to your setpoint.0 -
Vaporstats
So, how would you use the -1025 for boiler control if it makes on pressure rise?8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
The Honeywell L408J1025 ...
Is set up to be mis-wiring compliant- that is it can only be hooked up one way, which is make on pressure rise. Honeywell does this by taking a L408J1009, removing the lower (B) terminal screw and replacing it with epoxy. I have personal experience with this, as I was offered a L408J1025 at a can't pass up price, when I really needed a L408J1009. I carefully removed the epoxy from the terminal, ran a tap in it to clean it up, and moved the W terminal screw to the B position. But I digress. A L408J1009 is needed for controlling a steam boiler.
Here is the link to the literature on the L408J series
https://customer.honeywell.com/resources/Techlit/TechLitDocuments/65-0000s/65-0287.pdf0 -
oops..............
.....................All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Interesting
Very resourceful solution. I wouldn't have thought that was possible. On the pressuretrols I think they actually remove the terminal from the microswitch.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
Oh Superman...
Is a Vaporstat Kryptonite for Steamhead?!
Just kidding..."Hey, it looks good on you though..."0 -
Nope-
getting old and working too hard..........All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Better than the alternatives.
;-)Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
Follow-up two-wire vaporstat question
I'm also looking to replace a Honeywell 404a pressuretrol on a one-pipe steam system with a vaporstat. However, I can't find a two-wire vaporstat for steam. Does one exist?0 -
Vaporstat
The Honeywell L408J1009 will make or break the circuit depending on how it is wired. For Boiler control, you want to break the circuit on pressure rise to your setpoint. You would wire this with one wire to the top terminal and one to the bottom terminal. The vaporstat acts as a simple switch in the circuit, either allowing current to pass or not, depending on the pressure.
Eric0 -
Two-wire setup
Thanks Eric. That's exactly what I needed to know.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements