Rinnai E110C

Billjulian
Member Posts: 12
in Gas Heating
Installing this in my house. 6 zones. 2 are radiant. Question: with the low loss header as part of the provided package must I still connect my primary and secondary loops with the core tees (within 12 inches) as I would normally?
Thanks bill
Thanks bill
0
Comments
-
low-loss header
replaces closely-spaced tees in most installations. Primary is above the header, circ for that is inside the boiler on the Rinnai. Secondary is whatever pump you select for the job and whatever piping that supplies.0 -
Rinnai low loss header
Thanks for the reply I figured it replaced the closely spaced tees but was not sure. So I would pipe the system not connecting the supplys and returns whereas the LLH does this for me?0 -
not connecting?
Not sure what you mean by "not connecting."
P.19 of the installation manual clearly shows the proper configuration.0 -
NOT CONNECTING
What I mean is the LLH does the same thing as connecting the "spaced Tees" does? So I would not be connecting the spaced tees as I normally would had I not had supplied the LLH.0 -
correct
LLH replaces closely spaced tees, no need for them if it is installed.0
This discussion has been closed.
Categories
- 121.3K All Categories
- 84K THE MAIN WALL
- 2.9K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 417 Carbon Monoxide Awareness
- 40 Chimneys & Flues
- 1.7K Domestic Hot Water
- 4.7K Gas Heating
- 119 Geothermal
- 155 Indoor-Air Quality
- 3K Oil Heating
- 56 Pipe Deterioration
- 768 Plumbing
- 5.4K Radiant Heating
- 362 Solar
- 14K Strictly Steam
- 3K Thermostats and Controls
- 51 Water Quality
- 38 Industry Classes
- 73 Job Opportunities
- 17 Recall Announcements