NG fired steam boiler recommendation
SWEI
SWEI Member Posts: 7,348
A friend needs to replace his existing steam boiler and while we unfortunately have no real steam pros in the area, I do know one greybeard plumber that has done enough steam and will actually follow a manual.  Homeowner has a copy of We Got Steam Heat (thanks, Dan) and I will be reviewing the proposed piping and sizing with him before he signs a contract.
A 3-pass with a gas conversion would be great, but the plumber is not familiar with them and I think that's probably asking too much at this point, so I'd like to recommend something that can be bought as a package.  What say the pros?
thanks~
  • Rod
    Rod Posts: 2,067
    Installed EDR
    HI- What's the total EDR of the system?
    - Rod
  • SWEI
    EDR
    Don't have that just yet, but I suspect based on the size of the building and the age that we're looking at something in the 300-500 sq ft range.
  • kcopp
    kcopp Member Posts: 4,630
    I usually....
    install the Weil- Mclain EG series.
  • BobC
    BobC Member Posts: 5,539
    I'm not a pro
    but Smith is delivering the G8 with a Carlin EZ Gas power burner as one of the factory supplied burner choices. It should be no problem as long as the installer has a combustion analyzer.
    Mine gets installed Monday.
    Bob
    3PSI gauge
  • SWEI
    edited September 2012
    Smith G8
    Thanks - I'll look into that.
    I have a CA and will probably do the final setup.
    Edit: No mention of gas in the IOM - is there any documentation on this option?
  • BobC
    G8 and EZ Gas
    Smith does a great job of hiding this, let's see if I can get the pdf to attach to this msg. If not point your browser to - http://www.smithboiler.com/html/g8.asp
    Bob
    3PSI gauge
  • SWEI
    G8 with EZ-Gas
    Thanks - that brought up the brochure but I still can't figure out how you actually got there - they really did hide it.
    I'll call Smith on Monday and see if they can provide model numbers and an IOM.
    If this proves too rich for his blood, what would the next best choice be?  Steamhead?
    thanks~
    Steamhead Member Posts: 18,209
    Slant/Fin Intrepid
    with EZ-Gas would be my other choice.
    Give the customer a comparison of an atmospheric boiler's thermal efficiency against the G8 or Intrepid, and they'll likely go for it. Almost all of our customers do.
    Consulting
  • SWEI
    G8 with EZ-Gas
    Spoke with Smith yesterday and they said they are no longer shipping the G8 package, which explains the lack of info on their site.  Need to order with the -LB option (less burner) and source the EZ-Gas separately.
    My Slant/Fin rep was utterly convinced that the Intrepid was no longer available.  Slant/Fin is calling to educate them now -- I know we don't do much oil out west, but sheesh...
  • TomM
    TomM Posts: 233
    edited October 2012
    just bought a smith 8 series less burner with carlin ez gas burner last week.  due for delivery this week.
    -ain't too hard to slap it on and maybe make an orifice change VS prepackaged.
  • SWEI
    Efficiency comparison
    Anyone have numbers they can share with regard to this?  Nameplate ratings will certainly be helpful, but real-world fuel usage comparisons would rock.
    thanks!
  • JStar
    JStar Member Posts: 2,752
    Smith. Carlin.
    I'm going to be installing a Smith/Carlin steam job tomorrow. I'll post my combustion numbers. I'm going to keep a log of every boiler I install this year.
  • JStar
    edited October 2012
    Smith/Carlin
    Just finished this up today.
    86.2% efficient. Going back on a colder day to make the final adjustments.
  • JStar
    edited October 2012
    Pictures
    Pictures weren't working in th first post.
    Fnd the pictures on our Facebook page.
    http://www.facebook.com/media/set/?set=a.390182971050951.86827.353747484694500&type=1
