Smaller orifices?
Roland_18
Member Posts: 147
in Gas Heating
I couldn't help but notice that the I/O manual for my boiler lists smaller orifices on the parts page.
What would be the downside of downfiring ,say, 20% ?
I ask because the boiler is too big for my calculated heat loss. It was installed 7 years ago so I'm not in a hurry to change it out.
Thanks!
Thanks!
Orifices
Most burners are de-rated (reduced to lower capacity) when they are installed in high altitude locations due to the lesser amount of oxygen present in the thinner air. A simple way to do this is switching to smaller orifices.
If you de-rate a burner when you are not at altitude, the amount of excessive secondary air that will flow through the appliance will reduce the efficiency a fair bit.
There's lots to consider when you start making changes or adjustments to boiler like: the effect a change have on the heating of the heat exchanger, combustion efficiency, stack temperature drop, etc. All these things can shorten the appliances life, decrease the energy efficiency and possibly increase the amount of Carbon Monoxide present in the exhaust. So your best bet would be to hire a knowledgeable tech with the right tools. (like a combustion analyzer)There was an error rendering this rich post.