Hi all, I have read many post on this site, but still lost. 



I can do most of the piping and that about it....

Need assistance with wiring and choosing relays.



- I would like to have the steam boiler turn on to boil the water around 160 degrees, without making steam, when the basement thermostat is triggered.

After reading the many post at the site. I would like if possible some pictures of what type of relay? aquastat? and how I can tied it into my existing WellsMclean boiler.



Thank you in advance.

Comments

  • Mark N
    Mark N Member Posts: 1,115
    Hot water loop

    Click on the systems tab at the top of the page, then on hot water. Then click on condensate hot water heating. Your questions will be answered there.
  • Steamhead
    Steamhead Member Posts: 17,213
    Here is one such job we did

    this one is feeding an indirect but a baseboard loop would use the same hookup:



    http://www.heatinghelp.com/forum-thread/132567/One-of-the-worst-maintained-oil-fired-boilers-weve-seen



    Basically, you use the thermostat (or aquastat on the indirect) to operate a standard R845 relay. The line-voltage contacts on the R845 operate the loop circulator and the low-voltage contacts operate the burner. An aquastat breaks the low-voltage circuit between the relay and the burner if the water temperature gets too high.



    The main (steam) thermostat is wired to the burner in parallel with the loop relay circuit that goes thru the aquastat. In this way, the burner will run independently of the loop aquastat when the main house calls for heat.



    The loop aquastat is placed on a tee where the loop comes out of the boiler. This one has a long probe so it can reach clear thru the tee into the boiler section.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Help_Please
    Help_Please Member Posts: 3
    thanks...alittle more help

    Hi thanks for the assistance



    If possible please upload diagram or pictures for wiring the r845 and aquastat with the pump and boiler



    thanks again
  • JStar
    JStar Member Posts: 2,752
    Wiring

    Here's my copy.
  • Help_Please
    Help_Please Member Posts: 3
    Thanks for the picture

    Thanks for the diagram....

    It makes it so much more easier to understand



    Thank you

    Thank you