Ez Gas burner
I am installing a Ez gas conversion and can not get the flame sensor to prove a flame. The flame rod is not grounding on the end of the air tube and the gas preasure is correct. Is there a common problem I'm missing?
  • JStar
    JStar Member Posts: 2,752
    Flame sensor
    Did you check micro amps?
  • Paul48
    Paul48 Member Posts: 4,469
    Manual
    Grounding is one concern. Centered in the holes, and not closer to the edge than 1/16". Proper projection of the flame rod past the plate. Take it from a to z.
    Steamhead Member Posts: 18,209
    Two other things to check
    1- the burner chassis must be properly grounded, and
    2- if the air setting is way off for the firing rate you are using, the burner may not light.
    Consulting