Installing a secondary LWCO on Weil-McLain EG?
JohnNY
Member Posts: 3,290
I'm getting a lot of resistance and differing opinions from NYC inspectors about where to add a secondary manual-reset low water cut-off device and they're not accepting the installation manual's indicated "T" tapping as a viable location.
One inspector suggested one of these products, but it seems like overkill to me:
<a href="http://www.hydrolevel.com/new/index.php?option=com_content&task=view&id=22&bbc00e759205945763041cb2fb7e8b90=8defad515193547ce5430dba95e76854&Itemid=36">http://www.hydrolevel.com/new/index.php?option=com_content&task=view&id=22&bbc00e759205945763041cb2fb7e8b90=8defad515193547ce5430dba95e76854&Itemid=36</a>
<a href="http://www.hydrolevel.com/new/index.php?option=com_content&task=view&id=23&bbc00e759205945763041cb2fb7e8b90=8defad515193547ce5430dba95e76854&Itemid=37">http://www.hydrolevel.com/new/index.php?option=com_content&task=view&id=23&bbc00e759205945763041cb2fb7e8b90=8defad515193547ce5430dba95e76854&Itemid=37</a>
I'd like to see WM make a compliant second tapping available, but until then, your thoughts/methods are appreciated.
One inspector suggested one of these products, but it seems like overkill to me:
<a href="http://www.hydrolevel.com/new/index.php?option=com_content&task=view&id=22&bbc00e759205945763041cb2fb7e8b90=8defad515193547ce5430dba95e76854&Itemid=36">http://www.hydrolevel.com/new/index.php?option=com_content&task=view&id=22&bbc00e759205945763041cb2fb7e8b90=8defad515193547ce5430dba95e76854&Itemid=36</a>
<a href="http://www.hydrolevel.com/new/index.php?option=com_content&task=view&id=23&bbc00e759205945763041cb2fb7e8b90=8defad515193547ce5430dba95e76854&Itemid=37">http://www.hydrolevel.com/new/index.php?option=com_content&task=view&id=23&bbc00e759205945763041cb2fb7e8b90=8defad515193547ce5430dba95e76854&Itemid=37</a>
I'd like to see WM make a compliant second tapping available, but until then, your thoughts/methods are appreciated.
Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes
0
Comments
-
LWCO
I usually connect a top and bottom tap with a tee at the appropriate level for a secondary LWCO. Similarly, you can install tees on the sight glass valves, like a float type LWCO, and run a parallell pipe with a tee near the bottom 90.0 -
ok
Yeah, we did the top-to-bottom loop and that got rejected by an inspector. He wanted us to replace the switch in the #67 with a manual reset switch and add a probe-type operating lwco to the next higher tapping.
Annoying.
Most boiler companies give you a perfect tapping location for the secondary, but sometimes it's nice to have the tankless coil option the EG gives you.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements