have a Carlin (model 201 CRD) with an adjustable combustion head
it can change the firing rate from 2.5 gals to 5.5 gals per hr
is anyone familiar with adjusting the firing rate on these one stage burners - need to explore adjusting the burner due to short cycling (boiler is oversized)
also, since its oil, burner needs to be serviced and cleaned - dont think its been done for 5 yrs (boiler cleaned but not burner)
it can change the firing rate from 2.5 gals to 5.5 gals per hr
is anyone familiar with adjusting the firing rate on these one stage burners - need to explore adjusting the burner due to short cycling (boiler is oversized)
also, since its oil, burner needs to be serviced and cleaned - dont think its been done for 5 yrs (boiler cleaned but not burner)
0
Comments
-
Carlin 201CRD
If the boiler was cleaned, I doubt seriously that the burner wasn't cleaned and adjusted too.
Down firing burners doesn't always give you the results you expect.
You need a set of head positioning bars if you change nozzle GPH size. The head positioning bar properly spaces the retention ring in the end cone for proper combustion. You really need a digital combustion analyzer and know what you are doing to change anything.
If you are not a professional, you need to call one. And hope you get a good one.
The 201 CRD may not use head positioning bars for adjustment but may have markings on the burner housing. You need the manual to know where to set it. If you get it wrong, it will run like crap.0 -
burner too large?
0 -
burner too large?
burner that was installed on this weil mclain boiler is a 301 CRD 3 1/2 air cone,
the boiler cycles on and off continuously at lower pressures (its a< 1 ounce system)
the 301 CRD burner specs are 4.0 - 7.0 gals per hr, the boiler (series 80, model 681) is rated at 5.5 gals per hr
wouldnt the 201 CRD Carlin burner rated at 2.5 - 5.5 gals per hr be a better burner for this boiler. the 301 offers no meaningful opportunity to adjust burner to a lower gph setting (assuming boiler will work adequately at a setting below 4.0 gpm).
thanks0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements