Boiler Sizing
Steve Nichols
Member Posts: 124
Am getting quotes for replacing my original (i.e. very old) 1 pipe steam system boiler. I have done the EDR calcs based off of Dan's book. The house contains only convector units that are mainly recessed units. I have come up with 255 square feet of steam and when 1.33 pickup factor added in, I get 339 square feet. This equates to 81,556 BTU. The most recent contractor wants to put in a Burnham IN5 since he feels theload is too close to the upper limit of the IN4 (rated for 271 square feet @ 65MBH using the I=B=R Rating).
The IN5 ratings are (358 square feet of steam @ 86,000MBH using I=B=R rating). I am thinking this is too much boiler for my heating load, but I'm not a professional. I don't want this thing to short cycle but I'm not sure if I'm too close to the upper limit of the IN4 capacity.
Thoughts, ideas, comments?
The IN5 ratings are (358 square feet of steam @ 86,000MBH using I=B=R rating). I am thinking this is too much boiler for my heating load, but I'm not a professional. I don't want this thing to short cycle but I'm not sure if I'm too close to the upper limit of the IN4 capacity.
Thoughts, ideas, comments?
There was an error rendering this rich post.
0
Comments
-
dont add in any extra for piping
as that is already factored in by the factory as long as you use your actual square footage and size the boiler to its square foot rating. did that make sense?gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
So IN4 it is?
Thanks Gerry,
So, I should be okay if the square feet is up to the max. advertised IBR rating of the boiler? I'm just wondering how much "wiggle room" is needed for calcs that are off a bit. I'm close to the upper limit of the IN4 but well below the IN5. Just want to make sure I order the boiler that best fits my heating load.
Nice webpage on massive venting, by the way! I just ordered up some Gorton #1's to do my mains.There was an error rendering this rich post.
0 -
The smaller boiler should be just fine...
you have a load of 255 EDR and the boiler can handle 271. If they are lightweight copper/aluminum convectors, the pick up load is very light, so the 1.33 muliplier is probably very conservative, giving you even more extra capacity.There was an error rendering this rich post.
0 -
Thanks!
Heating Help forum to the rescue again.
Yes, they are the lightweight style, so I sized it right (yay).
Thanks Everyone for the much valued input.
SteveThere was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements