Pump curve testing ?
Paul_34
Member Posts: 31
I'm testing the pump curve on a grundfos ups 50-80/4 hooked up to 2.5" copper monoflow tee primary loop and my inlet gauge reading was 14psi and 22 psi at outlet of pump with all the zones calling for heat and with one zone calling for heat it was at 14 psi at inlet and 23 psi at outlet. The boiler has 14 psi in boiler. To get the head of feet number do i use 22 psi or 22psi - 14psi= 8psi to use. 1 psi=.43 head feet.
0
Comments
-
2.31
Ft of head per Psi....8 x 2.31 = 18.5ft of head....If that's the 115v version your moving about 10gpm on speed 2...Which a UPS26-99 can do at much lesser of a price...There was an error rendering this rich post.
0 -
#
its on speed 3 with those psi numbers. when i used speed 1 it went down to 19 psi.0 -
Ok
Still moving close to the same gpm..
http://net.grundfos.com/doc/webnet/versaflo/literature/L-UPS-PG-01_VersaFlo.pdfThere was an error rendering this rich post.
0 -
Pumpin Math...
It is the differential across the pump in PSI multiplied times 2.307 = the feet of head being produced under THAT condition...
ME
EDIT: Chris beat me to it. I should have checked before I answered.
METhere was an error rendering this rich post.
0 -
#
What pump would be a good match in a 2400 series taco.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements