Replacing a old Crane

fixitguy
fixitguy Member Posts: 95
After 15 years in the HPAC business, My first 2 pipe steam job and what a beauty. A 1948 Crane 198,000btu. Set up very nicely. I almost wish that I could replace the cracked section, but its time to say goodby. The customer has chosen a Peerless 63, a good choice for this application, I have installed quite a few of them in steam and hot water. The house has 250 sq ft of radiation and the customer wants to add another 100 to an addition. My quandry is what to use, a 03 or a 04L my instinct says the 04L, but will I be oversizing it to much?

Comments

  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,212
    edited July 2012
    radiation

    Make sure that the steam mains can handle the extra radiation. A 2" main should handle 350 edr with no problem.
  • Steamhead
    Steamhead Member Posts: 17,425
    Go with the 63-04L

    that way there won't be any issues when the addition is built.



    What kind of 2-pipe system is it?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • fixitguy
    fixitguy Member Posts: 95
    replacing a old crane

    Its a Richardson, nice and simple, and beautifly built
  • fixitguy
    fixitguy Member Posts: 95
    replacing a old crane

    adding another takeoff to a 3" drop header with 2, 2 1/2 risers shouldn't be a problem.
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,577
    edited July 2012
    Boiler size

    Is there a hi-lo burner for that boiler to accommodate the range of edr from present to future needs? Maybe Peerless has a "mod-u-pac" available.--NBC
  • fixitguy
    fixitguy Member Posts: 95
    hi-lo burner

    Great idea, not that I know of at the present time.