Here is the effect of to low a boiler water line
gerry gill
Member Posts: 3,078
that then exposes the bottom of the A dimension at the wet return to the bottom of the B dimension. The steam can be seen going down the A dimension pipe and slipping right around and coming backwards up the B dimension and shutting down the air vent on the return pipe. That part of the house then does not heat. Saw this in a new customers house today. The boilers water line needs to be about 2 feet higher. Its only been this way for twenty some odd years !
gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.
0
Comments
-
High waterline
Don't know the piping layout, but wouldn't lowering the wet return prevent steam short-circuiting into the dry return?--NBC0 -
yes, indeed..
lower the returns would work, a false water line would work, or put a replacement boiler on a pedestal would work..i'm bidding the boiler pedestal as there is a high water stain on the basement wall at about 18'' (and its on the boiler too) where the basement has flooded and submerged the boiler in the past..solve two problems at one time.gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
Pedestal
Gerry, what do you have planned for a Pedestal? Pour a pad 2 feet high? blocks?, Does anyone make pads for boilers? thanks0 -
IR Cameras
Thanks Gerry for posting the pictures! They really prove the old adage that "a picture is worth a thousand words!" What a wonderful diagnostic tool! I sure wouldn't be in the heating business without one.and I imagine being able to visibly show the customer the problem, makes big points and helps get the job.
- Rod0 -
We would use
solid concrete blocks for that job. I'll also have to build a small gantry crane to lift the boiler and put it on it.gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
Hi Rod -
yup, the thermal camera has been one of my better investments. (we wont talk about the things i thought would be great and turned out to be business blunders) . Makes for easy steam trap testing also..and yes, just as you say, the 'wow' factor with the customers is huge.gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
I-Pad
The latest I-Pad has a thermal imaging function. Not bad...write one off as a business expense.0 -
Thermal Imaging
Gerry, what make/model TI Camera are you using?0 -
its an older model,
Flir-Bcamgwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
Flir
Very cool Gerry, Flir has some deals on some refurbished cameras on their website, the prices have come down over the years.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements