industrial combustion klg

boiler_man
boiler_man Member Posts: 21
I've been struggling with the gas pilot. It seem that every few days I get a call that the burner is in saftey. I replaced transformer and I've cleaned the electrode and checked gas pressure which is 2 inches of water column.



If anyone has a clue as to what's going on please add your thoughts.

Comments

  • Paul48
    Paul48 Member Posts: 4,469
    Move

    this to the GAS section, and Tim will tell you how to fix it.
  • meplumber
    meplumber Member Posts: 678
    Need more info.

    What is the boiler/burner? BTU rating? Combustion numbers at startup and shutdown?



    Give us a little more and then we can help you.
  • meplumber
    meplumber Member Posts: 678
    My bad

    boiler-man. I didn't look at the subject line. The IC KLG's are pretty basic. Start with the pilot line solenoid. I believe it is an Asco solenoid. Check to make sure that the plunger isn't sticking. Then move to your pilot proving.



    I have a manual for that series burner, but I am not going to post it in an open forum. I don't want some facility maintenance guy making adjustments without the proper training.



    Contact me with the button under my screen name and I will see if I can get it to you.