Fill pigtail with water
Options
Fizz
Member Posts: 547
Recent post for low pressure gauge failure indicated possible cause to be failure to fill pigtail with water. Is this common practice?
0
Comments
-
Yes.
Some people count on condensation or splashing to fill the loop, but that's a bit risky.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
yes,
the water in the loop keeps the gauge from feeling the direct effect of the steam.gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
Yes
Thanks for info!
Fizz0