Commercial install
Henry
Member Posts: 998
Here is one of our larger replacements in a 71 unit luxury condo in downtown Montreal. It is a Smith G-28-HE-9. This one was done last fall after the previous boiler failed due to 1) improper piping that kept pulling the boiler apart and 2) too much chemical that ruined the faces. We did three steam heating boilers last winter that were killed by chemicals!
0
Comments
-
I am curious.
Did that gas pressure regulator right by the burner come with the boiler, is it required by the code, or did you just put it in because it was the right thing to do?0 -
Regulator
It is part of the burner. We reused the existing modulating "Power Flame" burner but reduced the pressure to 2 pounds. The existing Vacuum system is well, not functioning. The panels are shorted out. So the modulating valves for the two zones are modulated manually. We have a heat timer quote in to reestablish automation of the vacuums pumps, valves and boiler precession but due to the discovery of a leaking 5000 gallon underground oil tank, has been put off!0 -
why is the
steam takeoff in between the risers?gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
Piped wrong
As was stated earlier your steam supply should be after the two risers out of the boiler,not in between.
Why bother with a swing joint when it`s all welded?0 -
Certified instruction manual
Does ANYBODY read the manufacturers certified instruction manual? This is the way Smith wants this boiler piped. The swing joints prevent the boiler sections from being pulled apart as was the case previously. Each boiler company has a slightly different aproach to near boiler piping. We READ their manual and instruct our crews to FOLLOW the manual. We also have our own minimum standards regarding piping and pump installations.0 -
Welding
All piping over 2 inches, is welded in our steam installs! We might cheat sometimes when our welders and subs are busy, but only on hot water systems and only install with Victaulic systems! There will be NO threaded joint over 2 inches!0 -
Smith
Henry,
With all due respect where in the manufactures instructions do you see them telling you to install a bull head tee in between the two risers?
We read the instructions, did you?Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
That
piping does not agree with the manufacturers instructions and the instructions clearly say, swing joints must be employed. Risers and headers are called out as NPT,which indicates threaded pipe.0 -
I agree...bad piping
Even Smith's piping leaves something to desired for swing joinnts.
Only one Cast iron boiler manufacturer that I am aware of allows welded piping for mulitple riser connections to headers....and I see their boiler's failing all the time at the connections between the sections.
I am sorry, Henry, but that boiler should be repiped with threaded joints at the riser connections and with the system take off after both supplies. It is shown in the directions.There was an error rendering this rich post.
0 -
stirring the pot
I have been shying away from posting for a while but as others have stated that boiler looks incorrectly pipe to myself but in defense of henry i will take the other postion which is that i have seen boiler piped exactly as henry has pipe that one and they where piped that way about 100 years ago and suprise suprise it works perfectly even with 2 take offs taken off between the risers wonder never seise.Even myself once had to resort to taking my system take off between the riser on a larger weil 680 series because i would have had to repipe a very large percentage of the 4 inch main and would have had to thread in place .At the time i had no choice it was a emergency replacement in the winter did i have any issue due to the way it was piped no because i had like 4ft of vertical rise off my header there where no issue.To jump on the other side of the fence i use threaded pipe and fitting up to 6 inch and will work on some 8 but beyond that it is welded .As for weld headers evey one i have ran into in larger residental over 1 mbtu that was weld over time did cause the boiler to crack but each one was missing any compainion flanges which will reduce stress ,welded headers that i have seen that did not crack the boiler contained at least 4 compainion flanges on the near boiler piping just from the risers to the boiler header then either unions or compainion flanges for the reurn and systenm connections .Not to pick sides i would have to say i see more larger boilers piped the way henrys is in compairsion to the correct way whats wrong what right who knows peace and good luck clammyR.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating0 -
Don't mind me.
Munch munch munch.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
It
may work just fine. It will also provide very wet steam. It is a textbook "no-no" for near boiler piping.0 -
And here is the piping diagram
assuming the attachment works:All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
piping
Swing joints are required so as not to pull the boiler apart. There are also flanges on each outlet. To have the the riser going to the headder after the last outlet and not in between the two was not a choice. Some 6 feet above is a headder that devides the North and South parts of the building. To have to connect from the back would entail two days of welding which in winter, one does not have the luxury.With so much rise, the steam is ok even when the motorised valve modulate with the vacuum system. The system is completly silent.
I have done two to four such replacements nearly every year for over 36 years either during the winter or right after. Sometimes, one has to adapt to the situation. So far, I have never had to go back to repipe a system nor had a complaint about our instals. If something breaks like this Fridays Carlin on a steam boiler installed in February, we take the pill and make sure it running even if we can't get warranty from the manufacturer. The boiler produces hot water for a golf course.0 -
all that was needed....
to offset the system take off was to add one elbow and about 2 feet of pipe to offset the supply piping toward the back of the boiler. You may also have needed to move the rear boiler supply connection forward. I've done this a number of times and it only takes another hour or so.There was an error rendering this rich post.
0 -
Not impressed
As a homeowner what I essentially just read was "I didn't do it correctly because it would take too long".
I'm not impressed and I know there are a few pros on this forum who would NEVER have taken this approach.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Like this
which is on a much smaller boiler, but you get the idea. This was a job I did with my former company, and Gordo and I brought this customer to All Steamed Up.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Why?
We do it with threaded pipe all the time. Here are some examples. These pics go up to 4-inch, and we can go larger if needed.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
deleted
0 -
deleted
0 -
Let's all be nice
I know Henry was very haughty and belittling when he said "Does anybody read the instruction..." some people might say what ChrisJ said was justified...but let's try to respond to an attack by simply turning the other cheek.
otherwise, threads can start getting pretty heated...0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements