Making move to vaporstat

Fizz
Fizz Member Posts: 547
Will be adding vaporstat to boiler as I have Richardson vapor system.  Should pressurtrol be removed?  Also, what can I expect with change?

Comments

  • gerry gill
    gerry gill Member Posts: 3,078
    leave the pressuretrol and just

    wire the vaporstat in series with it. As to what to expect, its hard to say. Hopefully quieter operation but if you were building up pressure before you could actually short cycle the burner unless you have some tweaking on the gas valve done..or add two stage firing..
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,577
    adding a vaporstat

    i put mine on a manifold with a 0-15 ounce gauge, leaving the useless but required 0-30 psi gauge. make sure you mount it higher than the boiler, so that you will be able to do a skimming if needed [if mounted too low the elevated waterline will trip the vaporstat, and you will not be able to fire the boiler].

    if your venting is not top notch, you will see an elevated back-pressure, and short-cycling, [ as the boiler begins to make steam pushing the air out].--nbc
  • Paul Fredricks_3
    Paul Fredricks_3 Member Posts: 1,557
    venting

    Do you still have the original Richardson vent? If so it won't do enough venting for that system. We had a customer with a good sized Richardson, 4 zones. We calculated and added vents at the end of each main and return (the Richardson vent was already gone, but the existing vents were undersized). Helped the heat move about the system better and cut fuel costs about 10%.

    If you do have the Richardson vent and want to get rid of it, you can definitely throw it my way. Love to have one for the shelf. :)
  • Fizz
    Fizz Member Posts: 547
    Leave p'trol

    Why leave p'trol?  Also, if short cycle, what kind of tweaking on gas valve?
  • Fizz
    Fizz Member Posts: 547
    Leave p'trol

    Why leave p'trol?  Also, if short cycle, what kind of tweaking on gas valve?
  • Fizz
    Fizz Member Posts: 547
    venting

    Wish i did, but the original was replaced by vacuum vent.  Actually, my main vent is now Gorton #2, with a #1 on one dry return, and a maid o mist on other.  Is this enough? 
  • BobC
    BobC Member Posts: 5,505
    backup safety

    If you add the new vaporstat in series with the old pressuretrol the pressuretrol then becomes a backup safety. Lets say you set the vaporstat for a few ounces, it will cycle the boiler on and off if you exceed its pressure setting; the pressuretrol would only come into play if the vaporstat ever locked up. And that would save the boiler from destroying itself.



    For maximum safety see if you can mount the new vaporstat on it's own pigtail above the waterline of the boiler, then a single plugged pigtail can't disable both safeties.



    If your system regularly builds pressure towards the end of the heating cycle a two stage gas burner could prevent that from happening and save some fuel. With a two stage burner you would use the vaporstat to switch the gas burner down to it's low setting. the pressuretrol would then as as the safety.



    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • Paul Fredricks_3
    Paul Fredricks_3 Member Posts: 1,557
    Depends

    on how much supply and return piping you have, size and length.



    I use this to figure out what I need. It's a great resource:

    http://www.heatinghelp.com/products/Steam-Heating-Books/25/146/Balancing-Steam-Systems-Using-a-Vent-Capacity-Chart-by-Gerry-Gill-and-Steve-Pajek
  • Fizz
    Fizz Member Posts: 547
    Depends

    I have about 520 sf of radiation, and 120 of piping.  Thanks for the resource and advice.



    Fizz
  • Fizz
    Fizz Member Posts: 547
    Back-up

    Good advice.  Thanks.



    Fizz
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,577
    How much main venting

    Just keep adding vents until the back-pressure is down to a couple of ounces.--NBC
  • Fizz
    Fizz Member Posts: 547
    Brand of vaporstat

    What brand of v-stat, and where did you get it?



    Fizz
  • Rod
    Rod Posts: 2,067
    edited June 2012
    Vaporstat Models

    Hi- Attached is sheet with info on Vaporstats and the 408J manual. Since you have a vapor system, you will probably want to use the 0-16 ounce model. If you don't have one already you will also want an additional  gauge that will read low pressures well.  Either one that reads in ounces or a 0-3 PSI gauge.   The 0-30 PSI gauge should be left in place as it is required by code.

    - Rod
  • Fizz
    Fizz Member Posts: 547
    My mistake

    Actually have v-stat, i wanted brand of gauge and where purchased?  The v-stat i got is 1009 last 4 dig model.  thanks for info on v-stats though.
  • Rod
    Rod Posts: 2,067
    Gauges

    Hi -    Sources for Gauges  



    0 to 3 PSI    - The Gauge Store    http://www.gaugestore.com/prodinfo.asp?number=33020



    0 to 15 Ounces  - The Gauge Store   http://www.gaugestore.com/prodinfo.asp?number=33010



    For other size gauges  - The Gauge Store - http://www.gaugestore.com/products.asp?dept=1123



    For a 0-30 PSI replacement gauge - Pex Supply - http://www.pexsupply.com/Burnham-100325-01-Steam-Pressure-Gauge-for-IN-INPV-Boilers



    You may notice in the Wika Gauge literature that their gauges are only rated to 140 degrees so they will need to have pigtail to protect them from live steam. I’ve had the  0-3 PSI gauge on my one pipe system for three years now with no problems.

    - Rod
  • Fizz
    Fizz Member Posts: 547
    Gauges

    Great info!



    Thanks Rod.



    Fizz