Boiler wont fire unless..
Karamike
Member Posts: 6
in Oil Heating
Hello
Emptied boiler to install some baseboard
Was not able to finish due to schedule,so I isolated 2 heat zones and left DHW alone
Boiler will now only fire if I manually open zone valve for DHW?
Boiler is "Purepro" with Beckett burner
Any ideas help is appreciated
Emptied boiler to install some baseboard
Was not able to finish due to schedule,so I isolated 2 heat zones and left DHW alone
Boiler will now only fire if I manually open zone valve for DHW?
Boiler is "Purepro" with Beckett burner
Any ideas help is appreciated
0
Comments
-
I'm
not following you.........If the boiler is empty, do not fire it. If you have an indirect water heater, it uses boiler water to heat domestic hot water. If you dry-fire that boiler, you'll destroy it.0 -
Boiler was refilled
Filled boiler to 15 psi before boiler was fired
Boiler is equiped with Honeywell L7224 aquastat
Also,boiler will fire when basement heat zone is calling..but does not fire for DHW when temp drops unless I manually open zone valve for it
Any help is appreciated0 -
Do you have....
A coil for DHW, or an indirect?
If a coil, then you have to troubleshoot your control.
If you have an indirect, you may still have air in the piping, or once again, troubleshoot the controlThere was an error rendering this rich post.
0 -
Indirect
Superstor..0 -
How...
How many wires are going to zone valve? My guess is that you are not sending 24 volts to the valve or the valve head is bad. By manually opening it, you are closing the end switch. Which tells the boiler to fire.0 -
2 brown
with 3 white and 3 red wires connecting to zone valve0 -
Is there
A LWCO in the system?0 -
Ended up..
being a faulty aquastat on the domestic0 -
fix the problem
that is causing the zone valve not to open on temperature drop.There was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements