Commercial steam boiler - drain for summer?
elfie
Member Posts: 266
have a 15 section steam boiler and am wondering if it should be drained and left dry for summer and then refilled with fresh water?
have heard its not good because the existing water is pretty much deoxginated and therefore why get rid of it and introduce so much new oxygenated water
also, have some condensate lines that dont fully drain - worth draining for summer?
thanks
have heard its not good because the existing water is pretty much deoxginated and therefore why get rid of it and introduce so much new oxygenated water
also, have some condensate lines that dont fully drain - worth draining for summer?
thanks
0
Comments
-
Summer Storage
Hi- Having a commercial boiler, you might want to look at Rhomar Water's suggestions.
http://www.rhomarwater.com/products/residential-steam-system/ Take a look at their Boiler Pro 903 data sheet. If you have any questions, give them a call, they are nice people to work with.
- Rod0 -
drain steam boiler for summer?
anyone know if this is a good idea? to avoid rusting0 -
what about maintenance
If you drain it down now, all of the "mud" sitting in the mud legs and the low water cut-outs will have a chance to dry up and be extra exciting when you go to clean it out. Personally I would leave it filled. Haven't ever noticed this leading to rusting unless you have a leak on some of your piping. Then the leak should be repaired, draining the boiler isn't fixing the issue there.
Good luckMichael Knight0 -
No. its not a good idea.
Either press it up. (fill it into the header after adding chemicals to control corossion) or just turn off the switch and salute it.gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
filling up
I would like to do this to mine but I don't understand part of it. Whenever you add makeup water you have to bring it to a boil for a bit to boil all of the dissolved gases out.
How can I do this if I have it filled up into the header?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
No need to boil
Once you fill it to the headers, merely bring the temp up to 180 to 200 degrees. That's adequate to drive off the oxygen.
Then shut if off. Leave some clear indication on the power switch, breaker, or where ever, that the boiler MUST BE DRAINED to the normal water level BEFORE being fired again in the fall. You don't want to hear what that sounds like!Terry T
steam; proportioned minitube; trapless; jet pump return; vac vent. New Yorker CGS30C
0 -
I would lean strongly towards 200°.
At 180°, the oxygen content is about 3 mg/l. That's about 1/3 of what it is at room temperature, so depending on how much cold water was added, you might not even be getting rid of any of the oxygen you just added. Even at 200 you're only bringing it down to about 1.5 mg/l, so if you're not going for 200-210° F you might as well not bother firing the boiler.
On the other hand, 3 mg/l might be reasonably safe. I mean, if the water isn't saturated with oxygen I'm not sure the oxygen would attack the iron, so there isn't any need to fire the boiler anyway, which is probably why Gerry didn't mention it.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements