EDR Ratings for Thin Tube Radiators
MikeyB
Member Posts: 696
Looking for some EDR Ratings for some Thin Tube Radiators I have, the only chart i came across that had sizes/style close to the rads i have is the "Replacement Boiler Sizing Chart" . Cant seem to find them in Dans EDR book, but look like US Rads, if any one has some more info on this style of rad i appreciate it, there are no names or any other info on these rads. See attatched pics. Thanks
0
Comments
-
#sections X EDR = radiator rating
All you have to do is know how many tubes per section, how many sections, and how high. The boiler sizing chart has a section that is specifically for thin tube radiators on the second page, what part of that do you not understand?
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
EDR
I understand how to size the rads with that chart, just curious if anyone knows what brand they are.0 -
Hard to tell
Unless you find a name on any of the sections it could be hard to tell. A lot of different companies made thin-tube or slenderized radiators, and they all look pretty much the same. I have Burnhams and American Standards, and while I can tell them apart at a glance now, I never realized I had two different brands until I saw the raised lettering on one of them while I was cleaning it.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
Use
the Burnham Slenderized charts in E.D.R. By the time this type of rad came out the ratings were pretty much standardized.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
EDR
Thanks guys, I found the American Standard listings in the Library section, they seem like a good match as well0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 919 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements