SpacePak Thermostat Wiring

Attached is a pdf of what I have so far. What I am trying to do is make

the Duct Heater act as Emergency heat and Aux heat when the Goodman heat

pump goes into defrost. Should the L coming from the Honeywell be

connected to the L on the Duct heater? Should the E and Aux be jumpered

together on the Honeywell and then to the W2 on the Duct heater? What

contact on the Spacepak, if any, would be the white wire to the

Honeywell be? Is the Aux heat relay on the Spacepak used for anything?

Please let me know if any of the other wires would be incorrect?

Comments

  • Empire_2
    Empire_2 Member Posts: 2,340
    Depends

    While every manuf. is different, a diagram from the cond. and the electric heat would help.  "w" from the condenser???  is this powered when in defrost?  More info needed.  Everything you need should be in your internal equipment wiring diagrams.



    Mike T.
  • EddieG
    EddieG Member Posts: 150
    Wiring

    W (white) from the outdoor unit should go to the heater package. If you want the heater to energize when the t-stat calls for second stage, wire W2 or AUX to the heater package as well. The L is a service indicator. So it actually is a 24 volt input to the t-stat.