SpacePak Thermostat Wiring
bronze93
Member Posts: 1
Attached is a pdf of what I have so far. What I am trying to do is make
the Duct Heater act as Emergency heat and Aux heat when the Goodman heat
pump goes into defrost. Should the L coming from the Honeywell be
connected to the L on the Duct heater? Should the E and Aux be jumpered
together on the Honeywell and then to the W2 on the Duct heater? What
contact on the Spacepak, if any, would be the white wire to the
Honeywell be? Is the Aux heat relay on the Spacepak used for anything?
Please let me know if any of the other wires would be incorrect?
the Duct Heater act as Emergency heat and Aux heat when the Goodman heat
pump goes into defrost. Should the L coming from the Honeywell be
connected to the L on the Duct heater? Should the E and Aux be jumpered
together on the Honeywell and then to the W2 on the Duct heater? What
contact on the Spacepak, if any, would be the white wire to the
Honeywell be? Is the Aux heat relay on the Spacepak used for anything?
Please let me know if any of the other wires would be incorrect?
0
Comments
-
Depends
While every manuf. is different, a diagram from the cond. and the electric heat would help. "w" from the condenser??? is this powered when in defrost? More info needed. Everything you need should be in your internal equipment wiring diagrams.
Mike T.0 -
Wiring
W (white) from the outdoor unit should go to the heater package. If you want the heater to energize when the t-stat calls for second stage, wire W2 or AUX to the heater package as well. The L is a service indicator. So it actually is a 24 volt input to the t-stat.0
This discussion has been closed.
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 420 Carbon Monoxide Awareness
- 80 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 891 Plumbing
- 5.9K Radiant Heating
- 378 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements