Triangle Tube Solo 110 E-05

ptrick
ptrick Member Posts: 2
I have a 110 installed on an off grid system and keep popping an E-05 fault. I've changed the board and DHW sensor as per tech support, still haveing recurring error.

Comments

  • SWEI
    SWEI Member Posts: 7,356
    edited April 2012
    E-05

    Is an electrical interference fault.  Is this a modified sinewave inverter?  If so, you're going to need a power conditioner (that's not a surge strip, it's a big transformer-based filter) between the inverter and the boiler.  Either that or get a little pure sine inverter (Exeltech XP or similar) and dedicate it to the sensitive electronics, including the boiler.



    Check your AC line neutral-ground voltage & look for AC voltage on your sensor inputs as well.