expansion tanks on DHW systems
how important is an expansion tank on a residential or even light commercial system? i figure it could prevent some water hammer but can't think of other major reasons to add them to every installation. can anyone explain the physics of this issue for me, and help me become informed? thanks
  • icesailor
    icesailor Posts: 7,260
    Expansion Tanks:
    One word comes to mind, EXPANSION of water that is heated. The expansion has to have a place to go. If there are back-flow devices installed on the water service, you will have dripping DHW relief valves that cost many $$$$ to replace.
    Others more articulate than I will give you more reasons.
  • thanks for the reply.
    yes, i'm with you on that score, but wonder if the pressure diff between street (45-60 psi) will build enough to trip a 125psi setting on the t/p valve. i'm no ttrying to cut corners, just wanting to have a complete understanding of the physics. another quetion i have is given the temp diff from street to heater, how much pressure will build? thanks if you reply again.
  • icesailor
    Pressures:
    It depends on if your water system uses check valves on the meter sets. EPA considers municipal water systems to be pristine and protected water. Water in a house is considered of an unknown source.. Therefore, if there is any failure of the municipal water system, they don't water of an unknown quality to be introduced into the public systems. If the check valves are installed, you need a pressure tank.
    If you don't have checks, you probably don't need a DHW expansion tank.
  • Larry Weingarten
    Larry Weingarten Posts: 4,186
    edited April 2012
    water heaters...
    ... cause thermal expansion.  So you're dealing with the difference between say 50 and 120 degrees and the volume of the heater and hot side piping.  If the inlet is blocked with a back-flow preventer, pressure reducer or check valve, there is a real need for an expansion tank or a relief valve set only a little higher than line pressure.  If it's not there, all the plumbing in the house gets stressed, not just the hot side. We like to avoid stress!
    Yours,  Larry
    ps.  Icesailor is plenty articulate or he would not have used such a word  :~).
  • Toilet Valve can also solve the problem
    In researching this issue, I discovered this toilet valve:
    http://www.watts.com/pages/_products_details.asp?pid=7237
    When the water in the tank expands, this guy will just dump a little down the drain at 80 psi, say, instead of the 150psi setting of the T & P relief valve that is on the tank. In new construction, this saves a little money.
    When Denver suddenly required backflow preventers in multifamily buildings, all my water heaters started failing. Duh. The pressure swing from 60 to 150 psi a couple times a day did them in pretty fast. I think it causes a crack in the porcelain glass coating on the inside of the tank, and the unprotected steel tank rusts out in about 3 years.
    Just another one of the many unintended consequences of code requirements.
  • Mark Eatherton
    Mark Eatherton Posts: 5,875
    Sorry Kevin...
    But I think this idea is a terrible waste of our most precious resource, and I would never encourage anyone to waste water. Bad idea.
    To the original poster, there are pressure gages with a "memory" hand that will show the highest water pressure seen. It attaches to the drain valve of the heater, and if for example, the incoming pressure is around 60 PSI, but the hand show a peak of 120 PSI, then yes, you probably need a potable water expansion tank, and it is critical to air the tank diaphragm up to the static water pressure (60 PSI in this example)
    I had this very conversation with an AHJ this last week. The customers house didn't have a back flow preventer on the incoming service. He said that the requirement for potable water expansion tanks is required on ALL installations because there is the POSSIBILITY of a replacement water meter being installed, and all new meters have a check valve in their construction, hence the universal requirement on new installs.
    ME
  • I agree
    The other issue with the toilet valve pressure relief is that when it fails, nobody will bother tracking down the correct replacement valve, and then the water heater will have the same problem.