2 pipe radiator Q....
Options
kcopp
Member Posts: 4,630
Went to do a service call on what I was told was a HW heating system. Upon arriving the system was clearly a 2 pipe steam system. The radiator looks like it has been repaired many years ago w/ JB-weld or the like. The repair has failed. So in order to stop the water from making a mess I disconnected the radiator and capped it off. Much to my surprise there was a good deal of water in this radiator (3 gallons)..... Does this mean that the steam trap has given up the ghost and needs to be replaced? ty,kpc
0
Comments
-
I would believe so
otherwise the trap should have been open allowing draiange..it is also possible it is clogged with rust or gunk and is open but clogged..gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0