oil boiler to condensing LP gas Triangle Tube boiler

bob eck
bob eck Member Posts: 930
Home owner has old steel oil boiler with domestic coil and wants to put TT PE110 LP gas boiler in. Nat gas not available.

Oil btu is 139,000 per gallon and LP gas is 91,800 BTU per gallon

home owner will buy his LP tank so he can shop for competitive LP pricing

They have one heating zone 14,000 BTU copper baseboard

The addition to the house has radiant heat.

One radiant heat zone is 14,500 BTU

One radiant heat zone is 7,500 BTU

One padiant heat zone is 7,500 BTU

another zone copper baseboard zone at about 42,000 BTU but the heat loss in that zone is 25,000 BTU

will these small BTU zones effect the efficiency of this boiler?

home owner does not want to stay with oil.

any thoughts.

Comments

  • Paul Pollets
    Paul Pollets Member Posts: 3,663
    PE110

    the radiant zones will pipe through a 1"- 3 way thermostatic mixing valve and pump; the baseboard on its own pump. The primary loop must be 1" around the boiler and the 2 supply temps use closely spaced tees to work properly. The correct piping is described in their manual. Follow it carefully!!!!!



    Small zones will not affect the operation of the boiler. Use zone valves after the pump and use a "Smart" pump if possible. (Grundfos Alpha or Taco variable speed) The smart pump will "see" the zone valves opening and closing and adjust flow rates accordingly.