Drilling and tapping a main
Options
cn30
Member Posts: 34
I need to drill and tap a 1 ½” main to put in a vent; there are no plugs, no T’s, nothing, and old rusty pipe.
My question is, how small a hole can I drill and tap and still get decent venting? I ask because I’ve read that a Gorton D, at 1/8” (or ¼” straight), vents as much as a Gorton 1, with a ½” connection. Is that accurate? Is it all the orifice size? If so, why have such large connections?
If I can tap for ¼” I can get 18 threads per inch, or 27 threads per inch at 1/8”; given that the 1 ½” main is somewhere around 3/16 to .20 inches thick, but is curved, I could get at least 3 threads cut for a ¼” tapping, and maybe 5 for a 1/8” tapping. I would do the latter if I trusted that I would get adequate venting.
My question is, how small a hole can I drill and tap and still get decent venting? I ask because I’ve read that a Gorton D, at 1/8” (or ¼” straight), vents as much as a Gorton 1, with a ½” connection. Is that accurate? Is it all the orifice size? If so, why have such large connections?
If I can tap for ¼” I can get 18 threads per inch, or 27 threads per inch at 1/8”; given that the 1 ½” main is somewhere around 3/16 to .20 inches thick, but is curved, I could get at least 3 threads cut for a ¼” tapping, and maybe 5 for a 1/8” tapping. I would do the latter if I trusted that I would get adequate venting.
0
Comments
-
going to steam section
Sorry, I meant to put this in steam0 -
vent
forget about drilling. weld a boss on the main. with a ips tapping. perfect job.0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements