Pensotti gas conversion
jfplumr
Member Posts: 13
Today I converted a Pensotti BL5-125 from oil to natural gas. The listed input for this boiler is 177K. I am inputting 132K. My CO2 and O2 are right in the middle of specification but I am running .03" positive pressure over fire. Pressure at breech is .03" negative. This means the total loss through the boiler is .06". Is this normal and acceptable? I am concerned about running positive pressure over fire with a gas burner. The boiler is 5 years old and I don't think it had been cleaned until today. I thought I cleaned it very thoroughly but now I am wondering. Any ideas?
0
Comments
-
You'd need to check
with pensotti to be sure, but most gas power burners are rated to have positive pressure in the combustion chamber.
The draft being -.03 is that up or downstream from the barometric relief damper?0 -
Which gas burner
did you use?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
gas burner
Carlin ez-gas0 -
Should be OK
I believe that boiler was designed to run with a slight positive pressure over the fire. Check the I&O manual to be sure. The EZ-Gas and the Riello gas burners can fire positive-pressure boilers without difficulty, but the Midco burners cannot AFAIK.
What were the rest of the combustion numbers?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements