How much oil have I lost
I'm losing pressure in a solar Bray oil system, and haven't found a big leak. But how big a leak would account for this: I've lost 4 psi -from 16 to 12- in two months since repairing a cut line on the roof (long story). I have six each four-by-eight foot arrays, and three each one-by-two meter arrays. I've found a leak of about one drop in a week or two; how fast must a leak be to account for the loss I'm seeing? It's not in the heat storage tank (at least I don't think so, this oil is lighter than water, isn't it?)
0
Comments
-
total system volume?
it would be tough to guess without knoiwing how much the system holds, how much actually leaks, etc.
I would think any DHW coil or HX would have double walled heat exchangers and the oil would be visible, via a leak path, before it could cross into the potable water supply.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Bray oil next step
Thanks for the comeback. The oil -it's really a high temp hydralic fluid- is not getting into the house water. The fluid in the transfer tank is clear, no oil sheen. I've touched almost all the pipes, joints, and find no drip. It's a mystery I'd like to solve. Is there a sniffer like for natural gas? Someone who specializes in this?0 -
expansion tank
It may be leaking into the expansion tank. Is there any swings in the PSI or is it holding at 12?0 -
Pressure swings
The pressure changes with the temperature of the oil, from a low of twelve at night to a high in the low twenties during a sunny day. I've extracted the data for the residual pressure when the array temps are from below forty and plotted the accompanying pressure, as attached.0 -
pressure swings
It appears that the attachment dis not make my last post; I'm pasting the data here.
----------------------- Page 1-----------------------
Sheet1
Date Array #1 Pressure
38 16
38 16
33 16
31 16
Feb 03 27 15
31 15
27 16
Feb 04 38 16
Feb 08 17 14
31 15
Feb 09 28 15
32 15
Feb 08 17 14
31 15
Feb 09 28 15
32 15
Feb 10 30 15
26 15
24 15
Feb 11 24 15
Feb 12 16 14
22 15
22 14
Feb 13 26 14
28 15
34 15
32 14
Feb 15 32 14
34 14
30 14
Feb 16 37 15
31 14
32 13
24 13
Feb 18 33 14
37 13
28 12
Feb 19 25 12
25 12
24 12
24 12
27 12
32 12
34 12
Feb 20 30 12
35 12
Feb 23 28 12
Page 1
----------------------- Page 2-----------------------
Sheet1
Feb 26 17 12
Feb 27 38 12
Mar 06 30 12
Mar 10 32 11
Mar 13 39 12
Mar 19 26 12
Mar 20 28 12
Page 20 -
New Expansion Tank
It is more than likely your Expansion tank is failing or not sized properly. First check and make sure that the air bladder of the tank is pressurized to the pressure. If you keep your system at 30psi, then the bladder should be 3-5 PSI lower. I have seen the wild swings handful of times on systems. It not unusual for this to happen.
Always make sure the expansion tank is rated for solar temps.
Good luck
Michael0 -
Stable now, close the thread
I've checked every pipe, every joint, each array, and checked the tank and the heat exchangers. No oil leaks anywhere. Pressure has stabilized at 11-12 psi. How do I close this thread?0 -
Hydrin bladder a MUST....
If not, it WILL fail, eventually.
METhere was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements