Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Nest t-stat needs 24v

hotpipe
Member Posts: 24
A customer called today in a panic when his newly installed Nest did not work and the online customer support was of no help. A new 24 volt honeywell transformer and an unused 18/3 line later, and the heat was back on. The system is heat only, oil fired Olsen warm air that only had 18/2 to the Carlin primary. For the price of the Nest, perspective purchasers should take note and plan on calling a heating professional.
:)
:)
There was an error rendering this rich post.
0
Comments
-
Won't work on White-Rodgers 3-wire zone valves.
A neighbor called yesterday. She had just shelled out about eight Benjamins for three Nests. She was confused about a "black wire" and asked me what it was for. I told her the Nests won't work on her White-Rodgers zone valves and to take them back. I suggested she buy White-Rodgers1F80-0471s. She has older 1F97W-71s, but has trouble resetting them when she replaces the batteries.0 -
i would
Be interested to know what the amp draw is per t-stat, if one 40VA could handle multiple Nests.There was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements