Nest t-stat needs 24v
Options
hotpipe
Member Posts: 24
A customer called today in a panic when his newly installed Nest did not work and the online customer support was of no help. A new 24 volt honeywell transformer and an unused 18/3 line later, and the heat was back on. The system is heat only, oil fired Olsen warm air that only had 18/2 to the Carlin primary. For the price of the Nest, perspective purchasers should take note and plan on calling a heating professional.
:)
:)
Don't blame me, I voted for the old war hero and the business expert!!!!
0
Comments
-
Won't work on White-Rodgers 3-wire zone valves.
A neighbor called yesterday. She had just shelled out about eight Benjamins for three Nests. She was confused about a "black wire" and asked me what it was for. I told her the Nests won't work on her White-Rodgers zone valves and to take them back. I suggested she buy White-Rodgers1F80-0471s. She has older 1F97W-71s, but has trouble resetting them when she replaces the batteries.0 -
i would
Be interested to know what the amp draw is per t-stat, if one 40VA could handle multiple Nests.Don't blame me, I voted for the old war hero and the business expert!!!!0
This discussion has been closed.
Categories
- All Categories
- 85.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 424 Carbon Monoxide Awareness
- 73 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 130 Geothermal
- 160 Indoor-Air Quality
- 3.3K Oil Heating
- 61 Pipe Deterioration
- 885 Plumbing
- 5.9K Radiant Heating
- 376 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 59 Water Quality
- 49 Industry Classes
- 89 Job Opportunities
- 28 Recall Announcements