was told this wont work
stev0
Member Posts: 11
Comments
-
If its...
just baseboard why the primary /secondary? Seems overkill. It will work provided the end of the primary loop goes to the boiler....0 -
o
im going to ad 1more zone on the manifold. i did p/s because im going to use the optional buderus controls that ramp the boiler down and just wanted some insurance for the flu gas cond0 -
The piping layout
is fine, but if the boiler output is 94,000 btu, then you should be using 1 1/4 pipe, not 1 inch.0 -
point of no pressure change
I think the air scoop is backwards. in the photo the water should go from right to left on the primary loop.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
boiler piping
If it's the G115WS it's 1-1/4" supply, 1" return0 -
its a ga 124/23 1" supply &return
1"0 -
The only thing that I can see
worth mentioning might be
1. 1" pipe can carry about 75,000BTU so 1 1/4" might be a better choice..
2. Add a flow check on the secondary circuits to prevent that nasty Ghost flow..
Hope that I helped
:-) KCA:-) Ken0 -
Delta-T
A pipe size does not equate to btus it equates to gpm and gpm is based off that good ole hydronics formula. A 25 degree delta isn't going to hurt and you can move 7.5gpm thru 1" pipe.
gpm = btuh / ( delta-t x 500)
7.5gpm = 94,000 / 12,500
What's with the rainbow of circs?There was an error rendering this rich post.
0 -
no hot water zone?
Is there an indirect in this systems future?There was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements