hi got 94000btu in buderus cast iron boiler p/s setup im working on.pri loop is 1 inch both manifolds are also 1"  then reduced to 3\4 after flo chks to 3 baseboard loops anybody see any problems? thanks for any info

Comments

  • kcopp
    kcopp Member Posts: 4,462
    edited March 2012
    If its...

    just baseboard why the primary /secondary? Seems overkill. It will work provided the end of the primary loop goes to the boiler....
  • stev0
    stev0 Member Posts: 11
    o

    im going to ad 1more zone on the manifold. i did p/s because im going to use the optional buderus controls that ramp the boiler down and just wanted some insurance for the flu gas cond
  • furnacefigher15
    furnacefigher15 Member Posts: 514
    The piping layout

    is fine, but if the boiler output is 94,000 btu, then you should be using 1 1/4 pipe, not 1 inch.
  • Charlie from wmass
    Charlie from wmass Member Posts: 4,357
    point of no pressure change

    I think the air scoop is backwards. in the photo the water should go from right to left on the primary loop.
    Cost is what you spend , value is what you get.

    cell # 413-841-6726
    https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating
  • Tim P._3
    Tim P._3 Member Posts: 50
    boiler piping

    If it's the G115WS it's 1-1/4" supply, 1" return
  • stev0
    stev0 Member Posts: 11
    its a ga 124/23 1" supply &return

    1"
  • KCA_2
    KCA_2 Member Posts: 308
    The only thing that I can see

    worth mentioning might be



    1.  1" pipe can carry about 75,000BTU so 1 1/4" might be a better choice..



    2.  Add a flow check on the secondary circuits to prevent that nasty Ghost flow..



      Hope that I helped



      :-)  KCA
    :-) Ken
  • CMadatMe
    CMadatMe Member Posts: 3,086
    Delta-T

    A pipe size does not equate to btus it equates to gpm and gpm is based off that good ole hydronics formula. A 25 degree delta isn't going to hurt and you can move 7.5gpm thru 1" pipe.



    gpm = btuh / ( delta-t x 500)



    7.5gpm = 94,000 / 12,500



    What's with the rainbow of circs?

    There was an error rendering this rich post.

  • hotpipe
    hotpipe Member Posts: 24
    no hot water zone?

    Is there an indirect in this systems future?

    There was an error rendering this rich post.